Earth bonding cut for water meter

Discussion in 'Electrics UK' started by RMB, 27 Nov 2019.

  1. RMB

    RMB

    Joined:
    2 May 2005
    Messages:
    23
    Thanks Received:
    0
    Location:
    Hertfordshire
    Country:
    United Kingdom
    We recently had a water meter installed by the stopcock where the water supply enters the house. The installer cut the original earth cable that was attached and replaced it with a thinner one. The original cable came from under the floorboards and presumably was connected to the consumer unit. The new earth bonding doesn't actually go anywhere (see photo). I emailed the water company and they phoned to say this is correct. Is it? 1-S4060001.JPG 1-S4060003.JPG 1-S4060001.JPG
     
  2. Sponsored Links
  3. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    75,156
    Thanks Received:
    4,365
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    the wire they have put in is not a main bond, you still need one.

    the water co's earth maintains continuity each side of the meter, which might be plastic or could be removed.

    Is any part of your water pipe plastic?
     
  4. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,829
    Thanks Received:
    4,260
    Location:
    Retired to:
    Country:
    Portugal
    The cut wire should be connected to the pipe coming out of the ground.

    The wire they have put on is not needed.
     
  5. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,868
    Thanks Received:
    453
    Location:
    Kent
    Country:
    United Kingdom
    And why is there water all over it, is this a shower cubicle?
     
  6. RMB

    RMB

    Joined:
    2 May 2005
    Messages:
    23
    Thanks Received:
    0
    Location:
    Hertfordshire
    Country:
    United Kingdom
    @JohnD and @EFLImpudence Thanks for all your replies. I shall contact the water company. @SUNRAY - the pipe is in one corner and 3ft away is a shower cubicle. The water is condensation.
     
  7. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,868
    Thanks Received:
    453
    Location:
    Kent
    Country:
    United Kingdom
    Should that not be on the customers side of the stop valve? ie above the meter?
     
  8. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,829
    Thanks Received:
    4,260
    Location:
    Retired to:
    Country:
    Portugal
    No.

    You're thinking of the incorrect regulation/advice regarding gas meters.
     
  9. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,227
    Thanks Received:
    3,253
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    That depends upon whether one wants to comply with regulations or with electrical principles and common sense :)

    Kind Regards, John
     
    • Like Like x 1
  10. Sponsored Links
  11. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,829
    Thanks Received:
    4,260
    Location:
    Retired to:
    Country:
    Portugal
    Just realised - on a non-electrical matter -

    there is a branch pipe before the meter ???
     
  12. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,227
    Thanks Received:
    3,253
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    There does appear to be.

    Our setup here is exactly the same, the branch just upstream of our meter travels the entire length of our cellar to feed the neighbour's meter. I obviously have no idea as to whether the explanation is the same in the OP's case.

    Kind Regards, John
     
  13. DetlefSchmitz

    DetlefSchmitz

    Joined:
    17 Aug 2010
    Messages:
    2,224
    Thanks Received:
    293
    Country:
    United Kingdom
    If it were the case the stop cock would turn off the neighbour too. Is that what you have too John? I suppose it makes sense if there is a burst, but could be inconvenient for the neighbour.
     
    • Thanks Thanks x 1
  14. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,829
    Thanks Received:
    4,260
    Location:
    Retired to:
    Country:
    Portugal
    There is another stop tap between pipe and meter.
     
  15. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,868
    Thanks Received:
    453
    Location:
    Kent
    Country:
    United Kingdom
    I saw that branch but originally thought it passes behind the other. Does that mean only one branch into the property is metered?
     
  16. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,227
    Thanks Received:
    3,253
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Yes, but, just as with mine (and has EFLI has observed) there are stopcocks on both sides of the branch (in my case to the neighbour's). Hence one of those turns off the supplies to both properties, and the other turns off the supply just to mine. I would presume that there is another stopcock just before the neighbour's meter - so (in the event of their having a leak), they could turn off their supply without affecting mine (and, similarly, I can use the 'second' stopcock to turn off my house's supply without affecting theirs). Only if there were a leak in the pipe through my cellar (feeding the neighbour) would I have to use the upstream of my two stopcocks, thereby cutting off supply to both houses.

    Kind Regards, John
     
    • Thanks Thanks x 1
  17. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,227
    Thanks Received:
    3,253
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    As I've said, if it is like what I have here, the branch would go to the neighbouring property, where it is separately metered.

    Kind Regards, John
     