The disconnection of neutral only to start with was because my screwdriver was not long enough to reach the line, so socket removed and a connector block fitted to keep wires safe and separated, fitted where I had the USB socket, as wondered if the socket was faulty, trips too fast to measure earth leakage, but total earth leakage for whole house is high at the moment showing around 100 mA, but when I tried around earth wires nowhere near that high, that was the differential around the meter tails. I am not sure about the SPD and if that was reason for some odd reading? The lead was not clamped but was touching, and it was because of the SPD I was not using the insulation tester, but given up for a few days, not safe standing on a step-up working on the CU on my own.
But why an earth - neutral fault should show now, when CU has been fitted for 5 years, has me scratching my head, mainly as working out possible cause, may lead me to find the fault faster.
My first thought was a mains filter gone faulty, hence unplugging all I could. The earth leakage was 8 mA actually took a picture

so why now showing 100 mA don't know, 14 RCBO that's 12 type AC and 2 type A shed and faulty ring final on type A now, the 32 amp RCBO feeding back kitchen cooker had failed so had a new one in ready to change, so ring final one moved to cooker, and new one on the ring final, not as yet tested to see the ramp value, but since it was a handy ring final test my new RCD tester on, I know it was well within parameters and did not trip at ½ value, the problem is a set of steps between CU and the ring final sockets in question, so to reset have to walk outside and around the house to the flat under main house to reset, so really a job to do with two people.
I have a similar problem other side on the house, and last thing disconnected before it would reset was dishwasher, so though I would use insulation tester before buying new, and all OK, refitted all and tripping stopped, never did find the cause. The ramp test showed I had around 22 mA to spare, so not just on the edge of tripping.
So it does seem certain it is the neutral at fault, so what can change to cause a neutral earth fault? My thoughts were a multi-way extension with a filter gone faulty, but the two leads plugged in are not filtered.