It this installation providing an exported earth to the cabins, or are they all TT'd locally as well? That doesn't negate the need for RCD protection at the supply origin, I'm just interested.
Can't see rod and there are some really good earths taken from rods I worked at Point of Ayr gas terminal which connected to boards earth vie a resistor and had it's own earths rod and back-up generator and it's earth system was likely better than boards!
So need for RCD protection is more linked to earth fault loop impedance than on if TT or TN supply.
Can't see rod and there are some really good earths taken from rods I worked at Point of Ayr gas terminal which connected to boards earth vie a resistor and had it's own earths rod and back-up generator and it's earth system was likely better than boards!
So need for RCD protection is more linked to earth fault loop impedance than on if TT or TN supply.
Can't see rod and there are some really good earths taken from rods I worked at Point of Ayr gas terminal which connected to boards earth vie a resistor and had it's own earths rod and back-up generator and it's earth system was likely better than boards!
I have yet to come across a TT system which doesn't need RCD protection.
If you can tie down and the the Ze below 1 ohm then it might be possible but for reliability sake I still wouldn't trust it.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local