Earth Wire
6 Sep 2005
How do I know what size earth wire to be used for bonding. Is it down to the area?
Main equipotential bonding is the bond between the main earth terminal (MET) and other incoming services such as gas and water on a copper pipe install.
The size of the main equipotential bonding is determined by the type and size of supply TT, TN-S, TN-SC (PME).
For PME you need to ask your electricity supply operator for this info.
For 100A TN-S with a main earth conductor of 16mm² the main equipotential bonding conductor needs to be 10mm²
For a TT the main equipotential bonding must be at least half the size of the earthing conductor (rod - MET) and not less than 6mm
Supplementary bonding is the cross connection of all extraneous & exposed conductive parts in a location giving rise to increased risk of electric shock such as a bathroom.
See http://www.tlc-direct.co.uk/Book/5.4.3.htm
As a rule using 4mm2 for cross bonding pipes in your bathroom etc.
Upto 100A main supply should be 16mm2 Earth.
Old 60/80Amp supplys will be upgraded in the near future to 100A so install 16mm2 regardless
hi
just another option
you can bond the water and gas in 1 length of 16mm cable, as long as the cable is not cut at any point.
hth
matt
mattux said:
hi
just another option
hth
matt
Why 16mm²?
Spark123 said:
mattux said:
hi
just another option
hth
matt
Why 16mm²?
im not sure if you understood my post.
normally you would run a 10mm earth for the water and then another 10mm earth for gas. however it is acceptable to run a single 16mm to the water and then the gas(or viceversa) as long as the cable is continuous, ie not cut/broken anywhere including the first point of termination, in this case the first tenby.
matt
Correct me if I am wrong, but is it not the type of supply (TT, TN-S, PME)which dictates the size of the main equipotential bonding cable to use? I am also struggling to find the reg which says the cable needs to be increased to 16mm² for looped instead 10mm² (providing 10mm² is the correct size for the type of supply).