EICR results question

Joined
13 Nov 2008
Messages
1,551
Reaction score
31
Location
Avon
Country
United Kingdom
A test was carried out & a few points made.
One point was High resistance detected between ring final circuit protective conductors
I was advised one of the sockets would have a loose wire in the terminal hole or the screw has been screwed down partially on the wire & its plastic insulation.

He said he would need to unscrew every socket & look, 2/3 hours work.
Seems excessive time 2/3 hours as there isn't many sockets at all

Is there a tool i can buy to plug in each socket to advise me which socket it is.
I can then secure the screw correctly.

I'm capable of changing sockets no problem so just looking to go straight to the socket in question & rectify it.

The reading figure was 0.91

Thanks
 
Looking at the paperwork he left under ring final circuits i see the following.
I assume this is what your asking ?
Thansk

EaseUS_2026_09_25_12_43_20.jpg
 
Arr ok it does seem high it should be around 0.35 ish.

Just take the sockets off if there isnt many and re-terminate the earths.
 
Thanks.
So the earth is the issue in this case.

I suppose once ive done them all then there is no way i can check the reading & he will have to check when he does the other work.
 
Thanks.
So the earth is the issue in this case.

I suppose once ive done them all then there is no way i can check the reading & he will have to check when he does the other work.
No you won't be able to check without an ohm tester, let him check it if hes got to come back.

Hopefully you sort it and save a bit of cash.

Turn the power off when you do it obviously.
 
Ok i will switch off electric & check all earths.
I was thinking that there was a tool that you plug in the socket & when switched on get a reading.
If all sockets were lets say 0.3 & one was 0.9 etc then that socket is the one with the fault, either being check wire or just replace socket itself

Is there such a tool like that where once switched on a ohm reading is given ?
 
Are you saying for me to check wire size & advise as the reading might be ok & he didnt recognise it.

Thanks for your time.
 
Nope if it’s 2.5 / 1.0 would be

X and 2.5 X

still not high enough to give the readings but very few younger sparks encounter 2.5 / 1.0 so they don’t recognise it
Thats what im saying 2.5/1 the earth would be 0.47, 0.91 is too high.
 
Are you saying for me to check wire size & advise as the reading might be ok & he didnt recognise it.

Thanks for your time.

No. The reading for the CPC is abnormally high and should be be subject to further investigation

Why did you have the EICR?
Have you had a previous EICR?
Have any changes been made to this circuit? And this would include swapping sockets
 
Selling property.
I’ve changed some sockets over the years.
Only EICR done otherwise I’m unaware of this.
 