electric relay (coil) replacement 220/30 V

Discussion in 'Plumbing and Central Heating' started by gibson Ri59+!B+?, 18 Jan 2021.

  1. gibson Ri59+!B+?

    gibson Ri59+!B+?

    Joined:
    18 Jan 2021
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    looking for replacement coil for relay in Danfoss 57 H1 control box dimentions 37mm long 15mm dia.
     
  2. Sponsored Links
  3. oilhead

    oilhead

    Joined:
    29 Nov 2009
    Messages:
    2,052
    Thanks Received:
    489
    Location:
    Shropshire
    Country:
    United Kingdom
    I think you'll be looking for a long time. These units have been obsolete for 30 years. Replacing with a current Satronic box and base is simple and reasonably, though you'll need to replace the photocell as well.
     
  4. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    24,646
    Thanks Received:
    2,419
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Refurbished units seem to be available from HERE
     
  5. gibson Ri59+!B+?

    gibson Ri59+!B+?

    Joined:
    18 Jan 2021
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks Bernard,
    Yes noticed that site early on , sent them e-mail and tried phoning but outfit seems to have closed down . I've been in touch with Heating-Parts.co..uk in Bridgewater who have two Danfoss items which they say will function as replacements for the 57 H1 , should receive them tomorrow . The boiler was little used in the 45 years I've had it , the coil failed due to a 10kohm resistor going down to 9.12k . The boiler a Harcal 430 is built like a Boeing 747 and all the advice I've read was to try to hang on to it as today's replacements don't match up to it .Anyone with an old control unit of any manufature that contains a relay would suffice to provide the coil that I need to get this control unit functioning again .
     
  6. oilhead

    oilhead

    Joined:
    29 Nov 2009
    Messages:
    2,052
    Thanks Received:
    489
    Location:
    Shropshire
    Country:
    United Kingdom
    Your control box is the least of your concerns with a Harcol 430 if anything ever happens to the fan and motor, or the drive dog to the oil pump.
    Whilst the 'hang on to it' theory is valid for later standard efficiency boilers, this one will be quite inefficient.
     
  7. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,651
    Thanks Received:
    1,064
    Country:
    United Kingdom
    I used to convert to a Satronic TF 801 B and FZ cell which was same diameter as original.

    To OP I still have A static disc and Fan spacers if you need them !
     