Yes, based on what we have been told, simply cut the loop, and fit the sockets - brown to L, blue to N, earth to E.
You will need green and yellow sleeving on the bare earth wires.
Connecting up at the original socket is another matter.
I assume there are two old cables?
Is this a 32 amp ring circuit?
You see, if it is a ring circuit, the new wiring has to 'extend' the ring, which means at the existing socket one has to join one old cable to one new cable.
And then connect the other old cable to the other new cable directly to the socket terminals.
You will need to do a continuity test on the old cables to see if it is a ring, if it is a 32 amp circuit at the consumer unit.
EDIT. You mention plasterboarding was done - if those cables behind where the base units go got plasterboarded over, that's not great - as they are probably not in safe zones and so could easily get drilled through - as I think Eric and others have indicated.
You will need green and yellow sleeving on the bare earth wires.
Connecting up at the original socket is another matter.
I assume there are two old cables?
Is this a 32 amp ring circuit?
You see, if it is a ring circuit, the new wiring has to 'extend' the ring, which means at the existing socket one has to join one old cable to one new cable.
And then connect the other old cable to the other new cable directly to the socket terminals.
You will need to do a continuity test on the old cables to see if it is a ring, if it is a 32 amp circuit at the consumer unit.
EDIT. You mention plasterboarding was done - if those cables behind where the base units go got plasterboarded over, that's not great - as they are probably not in safe zones and so could easily get drilled through - as I think Eric and others have indicated.