Electricians Die

Remove the cutout fuse, which is it's primary purpose.

Silly question, but if the cutout fuse takes power away from the Line is there any danger between Neutral and Earth?
I only ask as I'm being brain washed (as a preventative measure) to beware of live Neutrals, although logic is telling me that occurs when there is a Line connected somewhere.
 
Silly question, but if the cutout fuse takes power away from the Line is there any danger between Neutral and Earth?
I only ask as I'm being brain washed (as a preventative measure) to beware of live Neutrals, although logic is telling me that occurs when there is a Line connected somewhere.
In terms of bs7671 neutral is a live conductor. But in terms of the dno only live is dangerous. So you need a double pole main isolator, but the dno don't.
Maybe they trust themselves not to get polarity wrong.
If all bonding is in place on a TN-c-S then with the line isolated the dno neutral will be the same potential as all your extraneous conductive parts anyway. In a tn-s there could be a difference depending what current is flowing in the local network.
 
In terms of bs7671 neutral is a live conductor. ... So you need a double pole main isolator, but the dno don't.
That's not quite true "in terms of BS7671" ....
If all bonding is in place on a TN-c-S then with the line isolated the dno neutral will be the same potential as all your extraneous conductive parts anyway. In a tn-s there could be a difference depending what current is flowing in the local network.
That is all true but, for reasons better known to it's authors, BS7671 regards single-pole isolation as adequate with both TN-C-S and TN-S (double-pole isolation only being needed with TT). Whilst I can understand their argument (which is actually stated in BS7671) in the case of TN-C-S, I am personally not quite so comfortable about TN-S.

If/when I need isolation in which I am totally confident, I have to say that I really want to see DP isolation (not the least because 'reversed polarity' is not unknown!), regardless of whether the supply is TN or TT!

Kind Regards, John
 
Fair enough didn't realise that, thought DP main isolator had to exist for all supplies.
 
Fair enough didn't realise that, thought DP main isolator had to exist for all supplies.
Ah, that's a bit different, and raises another inconsistency in BS7671 .... 537.1.4 requires a means of breaking the supply on load and isolation as near as practicable to the origin of an installation and then goes on to say (consistent with your comment) that a "main switch" intended to be operated by ordinary persons must be DP.

However, a couple of inches further down the page, in the section actually entitled "Isolation, 537.2.1.1 says "In a TN-S or TN-C-S system, it is not necessary to isolate or switch the neutral conductor ...."

So 'go figure'! I suppose we have to assume that what you say is actually correct, and that 537.1.4 is meant to over-ride the contradictory 537.2.1.1. I also assume that 537.2.1.1 is thinking primarily in terms of the Main Switch (or RCD incomer) in a CU, not anything which may exist upstream of the CU.

Kind Regards, John
 