Does anyone have experience with emporia energy monitors?
 
Basically wired as per image. However i have rcbo. I think because only one side of rcbo is wired its causing it to trip. Thoughts ?
 

Attachments

  • IMG_6360.png
    IMG_6360.png
    436.9 KB · Views: 146
Both L and N should goto the same rcbo
They don't appear to be RCBOs in the diagram we've been shown, since they don't have neutral connections in the diagram - so, if thst diagram correctly reflects what the OP has, your comment is presumably not really relevant?
 
Basically wired as per image. However i have rcbo. I think because only one side of rcbo is wired its causing it to trip. Thoughts ?
Could you indicate on your diagram (or explain) exactly what it is that is tripping?
 
I assumed the diagram was from the installation manual. And OP talked of rcbos.
Yes, I realised what you were thinking, but the situation is not clear.

As you imply, IF he does have RCBOs, then we need to know to what he has connected the three 'neutral' connections from his device, given that his neutral bar would presumably be pretty 'empty' in that situation.
 
Is that kit even approved for UK consumer units?
- Thinking, reds to the (correct) neutral bar, blacks to lives (as likely reds as browns), wire nuts (not seen those used in Britain for a very long time).
 
Is that kit even approved for UK consumer units?
Who knows - although it doesn't really need to be installed in a CU
- Thinking, reds to the (correct) neutral bar,...
If, as the OP has said, he has RCBOs, then none of the connections should go to any neutral bar (so not the 'correct' one)
blacks to lives (as likely reds as browns),
The colours are indded odd (at least in the UK)
wire nuts (not seen those used in Britain for a very long time).
Same here.
 
If you must use that product, the only sensible option would be to install it in an insulated enclosure, supply with with power from a 3A FCU, and attach the current clamp to the incoming line tail just below the electricity meter.

Shoehorning it into a consumer unit using the inadequate instructions provided is likely to result in problems, such as fire and death.
It was designed to be used in the USA, where service panels are typically much larger than UK versions, and where wiring colours, standards for connections and the like are totally different.
 