I don't think there is any requirement to main bond anything which is not, in itself, extraneous (to the premises).
But there is - 544.1.2 .... This states that even if the supply has an insulated section on/after entering the property it shall still be main bonded on the consumer side, i.e. the side that is not extraneous. No mention is made of the part which actually is extraneous.
In my opinion, most people are misunderstanding ('not reading properly'?) 544.1.2. As I read it, this is the section on main bonding
conductors, and indicates the required CSA and 'points of connection' (to bonded parts) of main bonding conductors
when they are required. To my mind, 544.1.2, per se, is (or should be!) saying nothing about what things
do need main protective bonding.
It is
411.3.1.2 which indicates what 'parts' require main protective bonding (using conductors per 544.1.2). It starts by saying that the MET should be connected by MPB to extraneous-conductive parts, and then adds "including....." with a list of five 'parts', including water and gas installation pipes. Maybe I'm wrong, but I've always regarded the 'extraneous conductive parts' at the start of that as being the over-riding consderation, with (i)-(v) merely being examples of things which
may (or may not) be extraneous-conductive parts. In other words, just because something appears in (i)-(v) that doesn't mean that it is necessarily an extraneous-c-p and, if it's not, then my interpretation has always been than MPB is then
not required. Is that not precisely how most people interpret (iv) in the list ("Central heating and air conditioning systems") - which, in domestic situations, will almost never be extraneous-c-ps and therefore are not normally main bonded?
I am trying to discover a reason for this. The only one I can think of is that (even though it is not extraneous (in its own right)) it is connected to extraneous parts by the boiler and it is 'belt and braces thinking just in case'.
As above, I have never believed that either 544.1.2 or 411.3.1.2 imposes a requirement to main bond anything which is not an extraneous-conductive part, not the least becasue that would be inconsistent with what I understand as the concept of main protective bonding. However, I agree with you in the sense that I have always regarded it as a confusing anomoly that 544.1.2 should talk about connections to something which is not an extraneous-conductive part in a section on MPB conductors (and which would therefore probably not count as main bonding per 433.3.1.2!)!
Do others not interpret the regs in the same way as me?
Kind Regards, John.