Expansion vessel pressure query

Discussion in 'Plumbing and Central Heating' started by ChrisOxford, 14 Dec 2009.

  1. ChrisOxford

    ChrisOxford

    Joined:
    25 Nov 2007
    Messages:
    491
    Thanks Received:
    60
    Location:
    Oxford
    Country:
    United Kingdom
    Hello everyone,

    Just a quick query regarding expansion vessels as used in a pressurised CH system with combi boiler, in this case, an Ideal Classic Combi FF280.

    The 8L vessel should have an initial charge pressure of 0.75 bar.

    The system design pressure is 1 bar.

    I suspect the expansion vessel may have lost some of its charge, though the diaphragm is definitely not perforated (no water coming out of valve).

    Is there any way I can check that the expansion vessel is correctly pressurised without draining down the system? If so, what kind of pressure should I expect if I connect a presure gauge to the "dry" side of the expansion vessel if the "wet" side is at 1 bar or so?

    Many thanks.
     
  2. Sponsored Links
  3. ollski

    ollski

    Joined:
    8 Oct 2003
    Messages:
    7,090
    Thanks Received:
    543
    Location:
    Bristol
    Country:
    United Kingdom
    No Chris you can't accurately check it with a force on the other side, if it's flat you will almost certainly be increasing your system pressure to well over 3 bar if you try and repressurize without releasing the system pressure. When we say drain down we don't mean a complete drain down, just a release of pressure. If you have time you can do this from a rad bleed....you will just have to keep doing it over and over again as you repressurize the ex. vessel.
     
  4. ChrisOxford

    ChrisOxford

    Joined:
    25 Nov 2007
    Messages:
    491
    Thanks Received:
    60
    Location:
    Oxford
    Country:
    United Kingdom
    Fantastic, Ollski, thanks for the reply. Good to know that I won't have to drain down fully.

    At the moment, the pressure seems to be too low when the system's cold, but too high when it's hot. The 3bar safety valve even opened on one occasion. Would this happen if the vessel charge pressure is too low?

    I also noticed some funny gurgling noises when the flexible hose that connects the vessel to the boiler was disturbed. Do they sometimes get blocked? Or is this probably nothing to do with the fault?

    Cheers,
    Chris.
     
  5. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page