.... Checked garage wires E-N still 1500Ω, E-N & L-N still O/C. .... At that point I've proved an unexpected low resistance E-N and L is clear, (>200MΩ) on the garage circuit.
I was in the house CU where tripping proplems were occuring and I proved a fault on the only garage circuit.
It also depends on what one considers to be low resistance compared to ∞, the IR test thinks it is.
Assuming the N-E link is immediately before the RCD I'll place a figure of 1mΩ, assuming the faulty circuit is my garage example of say 25m of 2.5mm² so in the order of ½Ω it doesn't take too much calculation to establish that in order to get 30mA in the fault will rewuire 500x30mA or 15A so yes it will trip under a modest current
Yes, I should have acknowledged that a trip could occur 'with a modest load current' in a TN-C-S installation if the N-E fault was 'relatively close' to the RCD.
However, perhaps we can agree that an N-E fault of a given impedance at a point on the circuit which has a given R1+R2 is much less likely in a TN-C-S installation than in a non-TN-C-S one ?
Yes, if the only load in the installation is on the circuit with the N-E fault, then essentially half of the neutral current will NOT go through the RCD - so, as you say,a load current of 60 mA should be enough to result in a trip
True, but I personally would not use the phrase "very low resistance" to refer to a situation in which all I knew was that the resistance was lower than an IR test could quantify.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local