External garage electricity wrongly connected to neighbours supply

1768664922454.png
Working with this
1768665182014.png
as the volts increase, so does the mA leakage, at 4 volts within limits, at 12 volts near the edge, and by 15 volts tripped.
 
Working with this ...... as the volts increase, so does the mA leakage, at 4 volts within limits, at 12 volts near the edge, and by 15 volts tripped.
Yes, but only because you have introduced a 500Ω N-E fault.

As I've written, if there were any loads on the installation, introducing such a fault path would cause the RCD to trip even if the N-E voltage were zero.
 