Ferroli Optimal HE plus 18OV heat only boiler

Well, I'm back again, boiler has been up & running fine since new PCB, until today that is. Boiler is now, I'd like to say kettling but I don't think its that. It's more like bubbling as though you have put a straw in a glass of water & started blowing into the glass. That's the only way I can describe it. Very weird bubbling sound, but does not lock out, just vibrates really bad until I turn it off. Checked condensate & is ok, not frozen, changed all microbore pipes to 15mm recently, removed & flushed rads, checked flue & noticed that the top half (plastic) has corroded away, not convinced this would affect the boiler this much. Anyone got any ideas?? Cheers peeps
 
Sponsored Links
Thanks Ian, disconnected the condensate earlier on to check if it was blocked & the pipes were clear. Did not check trap though, will check for blockages around that area. Cheers.
 
will be blocked further up, you really need a RGI to be honest, its not a DIY Job
 
Sponsored Links
Like I said, I'm ex gas, being registered won't make any difference. Disconnected pipe from boiler to top of condensate trap, blocked with whitish sludge. Cleaned out & refitted, easy enough, working ok now. Thanks for making me go back & re- check.
 