Sorry this is turning out to be a bit long ...
We have a problem with the heating system at church which I believe was caused by modifications, and then the system bodged to hide it.
The original system would have been coal/coke fired, and consists of the once common large pipes (2off 3") down each side wall with returns (2") down the sides of the aisles. These days it's a pumped system with a 60kW oil fired boiler. In addition, at the front (I suspect as a later addition) the flow goes through a large segmented radiator.
A few years ago, some fan-coil units were added and are plumbed in series with everything else - greatly adding to the heat output and de-stratifying the air, but at the expense of noise which means they get switched off during services/events. It's thought that at the same time the fan-coils were fitted, the pump was replaced with a larger one.
A while ago I noticed a check valve installed in the feed pipe from the F&E tank to the boiler - but until recently the penny didn't drop ... Then one day I happened to be outside when the system was heating up and noticed that one of the radiator vent pipes was dribbling and the penny dropped regarding that check valve. This is a diagram of the current system - I've separated out the radiators & fan coils for clarity, both sides of the system are identical. The dashed sections represent long sections that have been shortened to save space.
Obviously, with the check valve in place, the expansion can't go up into the F&E tank - so it has to go up one of the vent pipes and dribbles out. When the system cools down, the system fills up again with fresh water. Generally no-one had noticed as the system normally heats up and cools down when no-one is about.
So I thought about why that check valve was there, and my guess was that since the fan-coils and larger pump were fitted, there's too much resistance in parts of the system and the check valve is there to stop the water just being pumped up the feed pipe till the F&E tank overflows. So I tried removing the check valve - and sure enough, that's exactly how the system behaved
So clearly the people (apparently professional plumbers) responsible couldn't be ar**d to think about the problem and just bodged it and scarpered
So, having established that the pump pressure is just too high, I set about estimating the numbers. While heating up, the boiler manages about 10˚C delta-T, and so I estimated that the flow rate will be around 1.5l/s (5.4m³/hr) if the boiler is running at 60kW.
60kW / ( 4.2 kJ/(kg K) * 10 K )
I know it may well be less than that, but it seems that won't make all that much difference. Next I tried finding specs for the pump (Wilo SE150-N) but couldn't find any. Wilo's site has a "recommended replacement" function which suggested their Yonos MAXO 40/0.5-4 and the curves for that pump are :
So that would put the system somewhere around the red line I've added. With over 4 bar available, no wonder it's pumping back up the feed pipe Even turning the pump down to speed 1 leaves it pumping up - just not as fast.
First off, this is an area I'm not too familiar with - am I correct in taking that family of curves (like the red line I've added) represent different system flow resistances ? So where that curve intersects the pump performance curve (for a given pump speed setting) then that's the flow rate through the system.
So I've been thinking about ways to fix this. One obvious way is to raise up the F&E tank and the radiator vent pipes until there's sufficient head available to cancel the effect from the pump. That's probably not practical - I think the best we could achieve would be around 4-5 feet
So I'm thinking of adding a bypass and local circulation pump as shown here :
With this in place, the flow resistance round the main loop is considerably reduced - moving to the right on the pump performance curves and reducing the pressure differential in the system. Ignoring the locally pumped loop - it's just back to the old large bore cast pipes.
The local pump takes care of pushing the water round the fan-coil and radiator - and also some additional radiators we're thinking of adding.
Does the plan make sense ?
Anything I've missed ?
Any other suggestions ?
We have a problem with the heating system at church which I believe was caused by modifications, and then the system bodged to hide it.
The original system would have been coal/coke fired, and consists of the once common large pipes (2off 3") down each side wall with returns (2") down the sides of the aisles. These days it's a pumped system with a 60kW oil fired boiler. In addition, at the front (I suspect as a later addition) the flow goes through a large segmented radiator.
A few years ago, some fan-coil units were added and are plumbed in series with everything else - greatly adding to the heat output and de-stratifying the air, but at the expense of noise which means they get switched off during services/events. It's thought that at the same time the fan-coils were fitted, the pump was replaced with a larger one.
A while ago I noticed a check valve installed in the feed pipe from the F&E tank to the boiler - but until recently the penny didn't drop ... Then one day I happened to be outside when the system was heating up and noticed that one of the radiator vent pipes was dribbling and the penny dropped regarding that check valve. This is a diagram of the current system - I've separated out the radiators & fan coils for clarity, both sides of the system are identical. The dashed sections represent long sections that have been shortened to save space.
Obviously, with the check valve in place, the expansion can't go up into the F&E tank - so it has to go up one of the vent pipes and dribbles out. When the system cools down, the system fills up again with fresh water. Generally no-one had noticed as the system normally heats up and cools down when no-one is about.
So I thought about why that check valve was there, and my guess was that since the fan-coils and larger pump were fitted, there's too much resistance in parts of the system and the check valve is there to stop the water just being pumped up the feed pipe till the F&E tank overflows. So I tried removing the check valve - and sure enough, that's exactly how the system behaved
So clearly the people (apparently professional plumbers) responsible couldn't be ar**d to think about the problem and just bodged it and scarpered
So, having established that the pump pressure is just too high, I set about estimating the numbers. While heating up, the boiler manages about 10˚C delta-T, and so I estimated that the flow rate will be around 1.5l/s (5.4m³/hr) if the boiler is running at 60kW.
60kW / ( 4.2 kJ/(kg K) * 10 K )
I know it may well be less than that, but it seems that won't make all that much difference. Next I tried finding specs for the pump (Wilo SE150-N) but couldn't find any. Wilo's site has a "recommended replacement" function which suggested their Yonos MAXO 40/0.5-4 and the curves for that pump are :
So that would put the system somewhere around the red line I've added. With over 4 bar available, no wonder it's pumping back up the feed pipe Even turning the pump down to speed 1 leaves it pumping up - just not as fast.
First off, this is an area I'm not too familiar with - am I correct in taking that family of curves (like the red line I've added) represent different system flow resistances ? So where that curve intersects the pump performance curve (for a given pump speed setting) then that's the flow rate through the system.
So I've been thinking about ways to fix this. One obvious way is to raise up the F&E tank and the radiator vent pipes until there's sufficient head available to cancel the effect from the pump. That's probably not practical - I think the best we could achieve would be around 4-5 feet
So I'm thinking of adding a bypass and local circulation pump as shown here :
With this in place, the flow resistance round the main loop is considerably reduced - moving to the right on the pump performance curves and reducing the pressure differential in the system. Ignoring the locally pumped loop - it's just back to the old large bore cast pipes.
The local pump takes care of pushing the water round the fan-coil and radiator - and also some additional radiators we're thinking of adding.
Does the plan make sense ?
Anything I've missed ?
Any other suggestions ?