Hi John
Yes it takes around 9 minutes to drop to the anti hysteresis that I have set. If I set it any lower then yes it takes ages, but this way I’m guaranteed a drop no matter how long the boiler fires for.
The Valiant boilers anti cycle software obviously works differently
One of the main reasons for anticycling timing is to allow the flow temperature to fall sufficiently to avoid the boiler reaching SP+4/5C and burner trip after refirig, if it does trip then repeat recycle(s), some boilers do require 2 or even more recycles to get away, and thats with the full recycle time so difficult to see the logic in using the remaining recycle time as its very unlikely to get the boiler away, it would be interesting to set the hysteresis to say - 2C and set the time just a minute or so less than the actual observed time required to get the boiler away in one attempt and then see what happens on next or subsequent refiring(s).