I have recently had an Alpha HE25 safety checked, and the engineer informed me that whilst the boiler itself was perfectly fine, the flue had been installed within 300mm of the top left corner of the kitchen window, and so it had failed, and suggested that even though he couldn't force me to not use the boiler, if I did he recommended I keep the kitchen windows shut for safety (which I have).
My question is, what solutions are there to rectify this? I'm close to finishing the decorating and want to get moved in asap - can the flue be 'extended' to make the gases expel outside of the 30mm limit, or does the flue need to be completely moved?
Many thanks.