I thought fixed equipment in a bathroom is now 5s disconnection with greater emphasis has been put on local supplementary bonding? However if he is using MCBs then the efli should be such that the maximum amount of current required to operate the magnetic trip is achieved, hence in reality a 0.1s disconnection should be achieved.Stulz said:They must operate within 0.4s or 5s depending on the circuit. As this is a shower and the lower body resistance that would be intorduced by being immersed in a water stream, any protective device must operate to disconnect the circuit in the event of a fault within 0.4s.
Spark123 said:I thought fixed equipment in a bathroom is now 5s disconnection with greater emphasis has been put on local supplementary bonding? However if he is using MCBs then the efli should be such that the maximum amount of current required to operate the magnetic trip is achieved, hence in reality a 0.1s disconnection should be achieved.Stulz said:They must operate within 0.4s or 5s depending on the circuit. As this is a shower and the lower body resistance that would be intorduced by being immersed in a water stream, any protective device must operate to disconnect the circuit in the event of a fault within 0.4s.
Stulz said:Spark123 said:I thought fixed equipment in a bathroom is now 5s disconnection with greater emphasis has been put on local supplementary bonding? However if he is using MCBs then the efli should be such that the maximum amount of current required to operate the magnetic trip is achieved, hence in reality a 0.1s disconnection should be achieved.Stulz said:They must operate within 0.4s or 5s depending on the circuit. As this is a shower and the lower body resistance that would be intorduced by being immersed in a water stream, any protective device must operate to disconnect the circuit in the event of a fault within 0.4s.
Spark, you may be right there. I do not work in the domestic market and so my memory may be out of date on the disconnection time.
Regarding putting 6mm² T&E on a 45A breaker, I would urge against such a move. Even if you utilise good quality BASEC rated cable and take into account all environmental factors, your still on the fringe of acceptable loading capabilities for the cable. If, on the other hand, you buy the cheaper quality, non-BASEC approved cable, then you have no idea of the quality of the copper used, the insulation or the quality control utilised to maintain conductor size and quality. This may seem a trivial point, but are your really willing to risk your life, and that of your family for the sake of a few pounds and some effort to install the correct size cable?