I don't fully understand that.I recall a post (can't remember where, may have been piclist or electronics stack exchange) about design of a product (I think it was a medical device, not 100% sure) where they were having conducted EMC susceptibility issues with the capacitive touchscreen. To fix this they installed a common mode choke on all the supply conductors (including earth). However this added substantial extra resistance to the earth path, so they installed DP fusing to ensure adequate disconnection of earth faults.
I can understand that if things within the equipment increase the earth loop impedance (as seen from within the equipment) to a level which means that the circuit's OPD does not provide adequate fault protection, that one would need an internal OPD (fuse or whatever) within the equipment with a low enough rating to achieve the desired level of fault protection. However, I don't see why that, per se, would generate a need to fuse the neutral - so, provided that the polarity of the supply could not be reversed, I don't see why that would result in a need for DP fusing.
Medical equipment is, of course, a fairly special case, in which one often sees safety-related measures which go beyond what one would see in other equipment. However (again assuming that the supply polarity can't be reversed), I can't see why DP fusing would represent a "belt and braces" approach to safety - in fact, under certain complicated fault conditions, possibly even the converse.I think some manufacturers, particularly of medical equipment also install DP fusing as part of a "belt and braces" attitude.
Kind Regards, John