gledhill boilermate 2000
14 Dec 2010
West Midlands
hi all.
my gledhill boilermate 2000 is playing up.
when calling for hot water, either shower, bath, or kitchen, hot water flows for a few seconds then goes cold, then goes back hot, then cold !
just spent a few moments havng a look for anything loose in the gledhill unit and found all seemed ok. (connections etc)
what i did notice though was the hot water out pipe from the gledhill was going hot and cold. Also the pipe going out of the heat exchanger and into the unit was also going hot and cold !
does this indicate a faulty heat exchanger or could it be something else ?
Many thanks in advance !
Andy...................
Gledhill = sludge problems, nearly always.
WOULD cause your problem
Get it cleaned out and corrosion inhibited.
many thanks for fast reply !
also noted that the red LED on the PCB came on to red when the hot water was being called for, BUT it kept going out and then coming back on every twenty seconds or so.
is this normal or could it indicate a further problem ?
Many thanks,
The most common fault that cause this is the sensor on the plate HE.
I awlays replace this along with the return sensor, as these sensors are both unreliable.
Yon can get a basic check of the sensors by following the instruction book and pressing SW1 & SW2 in the correct order. You may get an ER displayed.
You could also check the DHW pump is running on HW demand and look to see if the HW demand 'dash' is lit on the display when there is a HW demand
If after changing the sensors the fault remains, then it could be the acb, but as these cost an arm and a leg, check sensors first