Glow worm Betacom 30 c bar light

Discussion in 'Plumbing and Central Heating' started by Catalin16, 1 Nov 2021.

  1. Catalin16

    Catalin16

    Joined:
    1 Nov 2021
    Messages:
    3
    Thanks Received:
    0
    Country:
    United Kingdom
    image.jpg
    Put pressure up to 1.6 ..still doesnt’t start . 60 bar light keeps going on and off
    Any help please ?
     
  2. Sponsored Links
  3. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    24,081
    Thanks Received:
    10,154
    Location:
    Livingston
    Country:
    United Kingdom
    Turn right hand control knob to 0 (12 oclock position) then tirn back to CH and HW position, does it now reset ?
     
  4. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    24,081
    Thanks Received:
    10,154
    Location:
    Livingston
    Country:
    United Kingdom
    That looks like a water drip there on the System flow isolating valve, if it is, then probably why your system pressure dropped in the first place

    Inkedleak_LI.jpg
     
  5. Catalin16

    Catalin16

    Joined:
    1 Nov 2021
    Messages:
    3
    Thanks Received:
    0
    Country:
    United Kingdom
    I have reset it and still nothing happens.
    The dripping was minor …really small .i dont think it was enough for the pressure drop . The drip is gone .

    What else should i try?

    By the way thank you very much for the reply.
     
  6. mcmoby69

    mcmoby69

    Joined:
    19 Jun 2011
    Messages:
    6,827
    Thanks Received:
    2,333
    Location:
    Lancashire
    Country:
    United Kingdom
    If you've been topping up often, the pressures sensor will be full of crud and not telling the pcb the correct pressure.
     
  7. Catalin16

    Catalin16

    Joined:
    1 Nov 2021
    Messages:
    3
    Thanks Received:
    0
    Country:
    United Kingdom
    Iast time i did top up was at least 2-3 months ago
     
  8. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    24,081
    Thanks Received:
    10,154
    Location:
    Livingston
    Country:
    United Kingdom
    try taking the cold pressure up to 2 Bar when cold and see if the boiler resets, you can lower the pressure again by releasing pressure from a rad bleed valve or drain point
     