Glow worm Betacom 30 c bar light

Joined
1 Nov 2021
Messages
3
Reaction score
0
Country
United Kingdom
image.jpg

Put pressure up to 1.6 ..still doesnt’t start . 60 bar light keeps going on and off
Any help please ?
 
Sponsored Links
Turn right hand control knob to 0 (12 oclock position) then tirn back to CH and HW position, does it now reset ?
 
That looks like a water drip there on the System flow isolating valve, if it is, then probably why your system pressure dropped in the first place

Inkedleak_LI.jpg
 
I have reset it and still nothing happens.
The dripping was minor …really small .i dont think it was enough for the pressure drop . The drip is gone .

What else should i try?

By the way thank you very much for the reply.
 
Sponsored Links
If you've been topping up often, the pressures sensor will be full of crud and not telling the pcb the correct pressure.
 
try taking the cold pressure up to 2 Bar when cold and see if the boiler resets, you can lower the pressure again by releasing pressure from a rad bleed valve or drain point
 