Just had a customer ring stating that their cxi 30 is leaking. From what I can gather off them it's coming from the little spout on the reduced pressure zone valve. Is this a common fault? Are they prone to leaking?
 
Sponsored Links
The RPZ valve will leak a little when the filling loop is operated.

If its leaking all the time the valve will need replacing (or the boiler pressure is higer than the mains and the loops been left open).
 