Thats' all OK, however when in CH mode and the boiler fires due to thermostat demand (actually from Glow Worm intelligent controller, situated in the hall), it starts with quite high heat - the temp ramps up quickly, and the boiler goes into anti-cycling. .
Dangermouse - I think I could solve my problem by increasing the pump pre-run time, i.e. before the boiler fires. Do you know if this is adjustable from the l2 menu and, if so, which parameter?
Interesting theory, Tony. You can monitor the flow and return temps via the LCD display. The flow ramps up quickly and the return is quite slow to increase. I may as well try a technical question to Glow Worm, via their website facility.
the ign system requires the fan speed to be at 70% of maximum to allow reliable flame spread accross the burner. You cannot get the boiler to fire on low rate then ramp up, it must be the reverse. The warmstart/preheat function is what I believe your getting confused with, this can be disabled.