Hi everyone, have hall/landing switches & both switches can operate either light.
Have trouble with the wiring.
On the old switch
Bottom L - R yellow to common
Red to L1
Blue to L2

Top
L- R
2 reds L1. blue/black L2
Yellow - common
Any help much appreciated
 

Attachments

  • IMG_4434.jpeg
    IMG_4434.jpeg
    493.8 KB · Views: 25
  • IMG_4433.jpeg
    IMG_4433.jpeg
    550.9 KB · Views: 22
  • IMG_4435.jpeg
    IMG_4435.jpeg
    496.6 KB · Views: 21
The only way it could trip out is if theres 2 different circuits in the switch, if so you mixed a colour up somewhere, double check.

Or you've caught a wire with the pin as you screwed it back.
 
As we look at the back of the switch the 3 wires in the right switch should be one cable.
As we look at the back of the switch the 5 wires in the left switch should be two cables.

However that's assuming it was wired like that originally.

Other than that it's damage as Pete says
 
Or you've caught a wire with the pin as you screwed it back.

One winter morning, I turned up on site (unoccupied house). The lights upstairs wouldn't work. The electricians had fitted the new face plates the day before.

It was pretty dark.

I loosened each face plate and inspected them.

One of the screws had indeed nicked a cable. I left that one dangling so that I could work. (The following day I used a heat shrink sleeve).

I then turned on the two gang 2 way hallway lighting. The CU tripped again.

I am not an electrician but spent time with a multimeter to rectify their errors.

I appreciate that the electricians are mates of the customer but WTF doesn't check to make sure that things are working before they leave?
 
WTF doesn't check to make sure that things are working before they leave?

Someone concerned for the welfare of their transport, which has been tied to the garden fence for hours, and really needs a bag of oats?
 
So this is what I found…. Thanks
 

Attachments

  • IMG_4455.jpeg
    IMG_4455.jpeg
    517 KB · Views: 6
  • IMG_4456.jpeg
    IMG_4456.jpeg
    458.6 KB · Views: 6
You've basically got 2 separate two way switches, one pair for the hall light, one for the landing light. Each pair are wired liked the image below.

With two sets, there is a higher likelihood of messing it up. There should be two pairs of wires that just go top to bottom of your stairs. Then there will be two lives (may be a single live feed linked across the back of one of the switches to power both switches/circuits). You'll then have two load wires (switched lives that go to the lamps), one at the top of the stairs, one at the bottom.

It will be a fairly easy job to undo all the wires, find out which one is the permanent live, which two pairs go from one switch to another and which two are the loads. With the power off and wires free, you can get a mate to help you "buzz out" the wires that go between the two switches, that'll get rid of 4 of them, then find the live, then the loads. A bit harder to measure the load resistance with LED fittings but if you have incandescent bulbs in them, easy peasy.

You've basically got two lots of this:

1795360654725.png
 
You've basically got 2 separate two way switches, one pair for the hall light, one for the landing light. Each pair are wired liked the image below.

With two sets, there is a higher likelihood of messing it up. There should be two pairs of wires that just go top to bottom of your stairs. Then there will be two lives (may be a single live feed linked across the back of one of the switches to power both switches/circuits). You'll then have two load wires (switched lives that go to the lamps), one at the top of the stairs, one at the bottom.

It will be a fairly easy job to undo all the wires, find out which one is the permanent live, which two pairs go from one switch to another and which two are the loads. With the power off and wires free, you can get a mate to help you "buzz out" the wires that go between the two switches, that'll get rid of 4 of them, then find the live, then the loads. A bit harder to measure the load resistance with LED fittings but if you have incandescent bulbs in them, easy peasy.

You've basically got two lots of this:

View attachment 427199
You've basically got 2 separate two way switches, one pair for the hall light, one for the landing light. Each pair are wired liked the image below.

With two sets, there is a higher likelihood of messing it up. There should be two pairs of wires that just go top to bottom of your stairs. Then there will be two lives (may be a single live feed linked across the back of one of the switches to power both switches/circuits). You'll then have two load wires (switched lives that go to the lamps), one at the top of the stairs, one at the bottom.

It will be a fairly easy job to undo all the wires, find out which one is the permanent live, which two pairs go from one switch to another and which two are the loads. With the power off and wires free, you can get a mate to help you "buzz out" the wires that go between the two switches, that'll get rid of 4 of them, then find the live, then the loads. A bit harder to measure the load resistance with LED fittings but if you have incandescent bulbs in them, easy peasy.

You've basically got two lots of this:

View attachment 427199
That’s a great explanation,, thanks very much!
 