Just changed over one of the radiator to a towel heated towel rail,
I drained the system, Changed it over then filled the system, the boiler now keeps cutting off, it sounds like there is air in the system with the gurgling noise. i have bled the radiators in order 1-5 with no luck. is there something else i should be doing? :cry:
 
Sponsored Links
Try bleeding the pump (release centre screw).
If that doesn't do it, maybe the Automatic Air Vent inside the boiler has blocked with scale.
 
Which one is the pump? i have stuck my head in the boiler, i'm a bit unsure of making a move unless i know for sure. is the pump the one on the left or the right? :confused:
 
Its probably the one that says Grunfoss! ( Might also be a Wilo though!

Look on the FAQ on this site for pumps and you will learn all about them and how to bleed them.

Tony
 
Sponsored Links
Thanks for all the help, it turns out that it was the Automatic Air Vent. All is well and we now have hot water and heating now.
All the best you you all.
Eean :D
 