Dear All,
Having read a few posts on here regarding this combi boiler, I've been through a few trouble shooting steps already.
From electrical power off and central heating off, switching on the power we have the green light on, the fan spins, then after about 5 seconds the red safety lock out comes on constantly. The boiler doesn't get as far as attempting to ignite.
The override switch has not been triggered. Pressure is 1bar+.
If I turn off the power and turn back on, then run a HW tap for a couple of seconds to trigger the HW flow switch during the start up sequence, the red lock out light doesn't appear, but the fan stays on.
If I then switch the central heating or a HW tap on the lock out will come on after a few seconds.
So far I have checked the fan pressure switch (by shorting the wires). Have also visually checked the the fan and assembly and it all seems clear. So I doubt the vent is blocked.
I have read you can bypass the main flow switch by simply removing the wires from the microswitch. However, this did nothing different. I also noticed that the small pin that is pushed out by the main flow switch diaphragm when the water is flowing was pushed out, even with the system off. I pushed it back in manually and it remained in place even when the system was restarted. i.e. not pushing the microswitch.
Does this mean either there is no flow (i.e. pump fault or PCB fault stopping pump from running) or the diaphragm has failed.
If the diaphragm has failed then why doesn't bypassing the flow switch allow the system to get to ignition (or is this check incorrect - I suspect and hope it is). Is there any easy way to tell if the pump has failed. Feeling the pump there is little if any vibration at any point. But presumably the pump won't start unless the flow switch works.
I tried to check the diaphragm but wasn't able to isolate the flow, so water was still under pressure and as some idiot installed it directly over the mains fuse box I stopped
!
Just to confirm to isolate and drain the boiler for changing the diaphragm on the main flow switch. I need to close the inlet and outlet for CH, I assume the cold water in doesn't need to be shut off, but I shut it off anyway. I then opended the drain valve on the central heating flow on the boiler. The pressure dropped to about 1/2 bar and then was reduced to a drip. To me it looks like the CH flow or return valves aren't shutting properly? Which means I need to drain the entire system? Whn I reopened the valve the pressure remained at 1/2 bar which again indicates to me the valves aren't closing fully. Any pointers on this most welcome. Both flow and return did seem to be very stiff, but were turned fully 90 degrees as indicated in the manual.
Many thanks for any help or advice.
Also, for anyone interested the service and installation manual can be found here for free http://manuals.aonly.com/index.php?d=Boilers/Halstead&f=HALSTEAD FINEST GCNo.47-333-06.pdf
Thanks,
Toby
Having read a few posts on here regarding this combi boiler, I've been through a few trouble shooting steps already.
From electrical power off and central heating off, switching on the power we have the green light on, the fan spins, then after about 5 seconds the red safety lock out comes on constantly. The boiler doesn't get as far as attempting to ignite.
The override switch has not been triggered. Pressure is 1bar+.
If I turn off the power and turn back on, then run a HW tap for a couple of seconds to trigger the HW flow switch during the start up sequence, the red lock out light doesn't appear, but the fan stays on.
If I then switch the central heating or a HW tap on the lock out will come on after a few seconds.
So far I have checked the fan pressure switch (by shorting the wires). Have also visually checked the the fan and assembly and it all seems clear. So I doubt the vent is blocked.
I have read you can bypass the main flow switch by simply removing the wires from the microswitch. However, this did nothing different. I also noticed that the small pin that is pushed out by the main flow switch diaphragm when the water is flowing was pushed out, even with the system off. I pushed it back in manually and it remained in place even when the system was restarted. i.e. not pushing the microswitch.
Does this mean either there is no flow (i.e. pump fault or PCB fault stopping pump from running) or the diaphragm has failed.
If the diaphragm has failed then why doesn't bypassing the flow switch allow the system to get to ignition (or is this check incorrect - I suspect and hope it is). Is there any easy way to tell if the pump has failed. Feeling the pump there is little if any vibration at any point. But presumably the pump won't start unless the flow switch works.
I tried to check the diaphragm but wasn't able to isolate the flow, so water was still under pressure and as some idiot installed it directly over the mains fuse box I stopped
Just to confirm to isolate and drain the boiler for changing the diaphragm on the main flow switch. I need to close the inlet and outlet for CH, I assume the cold water in doesn't need to be shut off, but I shut it off anyway. I then opended the drain valve on the central heating flow on the boiler. The pressure dropped to about 1/2 bar and then was reduced to a drip. To me it looks like the CH flow or return valves aren't shutting properly? Which means I need to drain the entire system? Whn I reopened the valve the pressure remained at 1/2 bar which again indicates to me the valves aren't closing fully. Any pointers on this most welcome. Both flow and return did seem to be very stiff, but were turned fully 90 degrees as indicated in the manual.
Many thanks for any help or advice.
Also, for anyone interested the service and installation manual can be found here for free http://manuals.aonly.com/index.php?d=Boilers/Halstead&f=HALSTEAD FINEST GCNo.47-333-06.pdf
Thanks,
Toby