Darned confusing this cable size lark...
I was checking my new shower circuit for a 9.5kw shower - just received certs for it (thanks to all here for info) and it appears to be a 13mm w x 7mm h on the pvc sleething - tape measure job of the measurement.
So, by my reckoning (and use of http://www.wiki.diyfaq.org.uk/index.php?title=Cables ) this would suggest that this is 6mm2 cable.
Now that sounds like it aint enough for a 9.5kw shower on a 45A fuse. But I looked a bit deeper and saw that it depends on it's installation method - notated from A - E, as this is a new cable run, solely for the shower, up a cavity in a non-insulated wall, above the lagging and joists in the loft and down a stud wall (again a cavity), this is ok as it's a 'C' type installation that is rated to 47A ? It's a T&E cable.
Cert with the test info on this seems to back this up, and the cable is definitely stranded.
Would it be better to swap it out for 10mm just in case ? I wouldn't want my new shower tripping.
I was checking my new shower circuit for a 9.5kw shower - just received certs for it (thanks to all here for info) and it appears to be a 13mm w x 7mm h on the pvc sleething - tape measure job of the measurement.
So, by my reckoning (and use of http://www.wiki.diyfaq.org.uk/index.php?title=Cables ) this would suggest that this is 6mm2 cable.
Now that sounds like it aint enough for a 9.5kw shower on a 45A fuse. But I looked a bit deeper and saw that it depends on it's installation method - notated from A - E, as this is a new cable run, solely for the shower, up a cavity in a non-insulated wall, above the lagging and joists in the loft and down a stud wall (again a cavity), this is ok as it's a 'C' type installation that is rated to 47A ? It's a T&E cable.
Cert with the test info on this seems to back this up, and the cable is definitely stranded.
Would it be better to swap it out for 10mm just in case ? I wouldn't want my new shower tripping.