Heat going off too soon - please help!

Discussion in 'Plumbing and Central Heating' started by Mintachine, 22 Oct 2018.

  1. Mintachine

    Mintachine

    Joined:
    21 Oct 2018
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi all, I spent the past few days trawling these forums to find the answer with no luck so hoping someone can help.

    Just got a new gas combi system, so all new boiler, rads, pipes etc.

    The thermostat and an 'always on' radiator are in the hall. This rad is reaching the stat temp so quickly that the heating goes off while the other rooms are only just starting to warm up.

    Is there anything we can do to correct this ourselves? Thank you.
     
  2. jj4091

    jj4091

    Joined:
    1 Dec 2006
    Messages:
    4,417
    Thanks Received:
    353
    Location:
    Cumbria
    Country:
    United Kingdom
    I am not a professional heating engineer, but when we had the same problem I closed both of the hall valves completely & then just cracked them open to allow the water to flow. A heating engineer who visited later recognised what I had done & did not say I had done the wrong thing or suggest another cure. Whether this will help you or not I am not sure, but I would guess better qualified engineers will help later.
     
  3. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    10,709
    Thanks Received:
    2,052
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Call your installer back to sort it - the stat should be in a suitable location and he should have balanced your system as part of the installation
     
  4. RayCaister

    RayCaister

    Joined:
    31 Mar 2017
    Messages:
    83
    Thanks Received:
    14
    Country:
    United Kingdom
    1 Turn up the tenp. on the thermostat.
    2 Turn down the flow on the hall radiator.
    3 Get the installers back to explain the system.
     
  5. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    5,213
    Thanks Received:
    1,002
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    The thermostat is located in the wrong place, or the hall radiator is too large. This is a system design mistake by the installer, so they should rectify it.

    There are basic room thermostat location requirements:
    • It should be in a place that is the last to warm up, so that the radiators remain 'on' in all of the other rooms first to allow them to heat up before the main thermostat turns the whole system off.
    • Not in a room where it will be subject to other heat sources such as cooking appliances, fireplaces & sunlight etc.
    • It should be located in an open space to allow air to circulate freely around it so that it senses the true ambient temperature of the room in which it is located, not stuck in a corner, behind curtains or furniture, or subject to drafts
     
    • Thanks Thanks x 2
  6. Mintachine

    Mintachine

    Joined:
    21 Oct 2018
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Thank you all for the responses and advice.

    stem, the thermostat isn't in the coldest room (which would be the entrance hall downstairs), and it is certainly possible the rad is too big for the space.

    The installers are coming back tomorrow to 'calibrate' it as he put it, hopefully they'll sort it.

    Thanks very much. (y)
     
  7. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page