Heat Line VISO 24 DHW Issue

Joined
7 Nov 2010
Messages
5
Reaction score
0
Location
Manchester
Country
United Kingdom
I have inherited the boiler with the property. Heating comes on OK with timer or manually and gives good heat. The Domestic Hot water is however a problem as when the tap is on full bore it only then starts to heat and is very cool.
My first instinct is the Flow Sensor as I have had a previous boiler with a similar issue however this boiler is considerably different to anything I have had before and there looks to be only one sensor of this type in the Viso 24.
If it was a thermistor issue I think we would have no hot anything or too hot so need urgent advice to get this working before the cold weather bites !
Suggestions please.
http://www.heatline.co.uk/boilers/assets/products/manuals/Vizo 24 and 28 manual.pdf
 
Sponsored Links
The mains water pressure is quite high so on full bore it will fill a bucket very quickly but with barely warm water.
Have to take care to point down plug hole or risk of soaking everything in area.
At a rate that is useable to say wash your hands I don't hear the boiler start up.
 
Turn heating off.

Set hot tap to give 9 litres per minute and measure temperature.

Tony
 
Sponsored Links
A simple test like that can identify the presence of several different faults, either singly or together.

The most obvious is wrong gas settings, a blocked secondary or a scaled primary.

Or the most likely perhaps that the owner has too high a DHW flow rate!

Tony
 
After checking the flow rate isn't too high as mentioned, the next most common fault I find when theres a Hot water problem on these is the HW thermistor.

It's very difficult/ impossible to get to without removing the left hand casing.

This involves exposing the combustion chamber so its an RGI job.
 
Most likley a sticking aquasensor p/n 0020061630; however this boiler will only provide sufficient DHW at 9.5 l/min - both need checking.
 
Most likley a sticking aquasensor p/n 0020061630; however this boiler will only provide sufficient DHW at 9.5 l/min - both need checking.

Are Heatline good boilers? Some on here say they are not. I have heard they are good and cheap.

The problem at hand. In this case is it worth putting in a 10 litres per minute flow regulator before the combi so the tap cannot be turned up beyond the capacity of the combi?
 