If it was a thermistor issue I think we would have no hot anything or too hot so need urgent advice to get this working before the cold weather bites !
These usually fail safe so you usually get lukewarm water!
Best advice is to check out that thermistor because that is the most common cause of this type of problem.
You could play about getting a reading of the resistance if you want. Its a PITA
JUST FOR TESTING!
I would just disconnect the DHW thermistor wire from the thermistor and the boiler will run safely while you run some water test it on the primary thermistor .... We know this is ok because your heating works fine.
If you get hotter water then that points to the DHW thermistor
Don't be tempted to leave it like that as you have temporarily taken out a line of defence against scalding.
Then get an RGI out to fit a new one
Also check that no one has knocked the gas valve [ECV] partially closed as a restriction in the gas supply can cause the problem.
Many a time I have been called to similar problems to find that someone has thrown something into the gas cupboard and knocked the valve.
Quite often DIYers get their hands on these boilers because they can be bought in B&Q, then they expect it to work on an undersized gas pipe. You need a good flow of gas to heat that water as it passes through the boiler. Much more than for heating.
I wouldn't have thought the flow sensor was at the root of it because the boiler wouldn't fire if that didn't work.
Yes there's other causes but start with the common and the easy stuff
Ive never seen a blocked plate heat exchanger on one of these yet. There's a filter on the return that would block up long before that did
ye god's it's alive icon_razz.gif icon_razz.gif
must be dark icon_lol.gif
Yes Kev m8 I am truly nocturnal again
PS If you want to see a better copy of the MI's with a full display of the fault finding look up Glow worm betacom C .... its the same boiler with a different frock