Heating Thermostat

Ref

Joined
9 Jul 2012
Messages
5
Reaction score
0
Location
Northamptonshire
Country
United Kingdom
Hi,

Can any body help. I damaged my room thromostat moving furniture so I replace it with a Wickes standard thermo the thermo has 4 connections same as my old one but I cant remeber the wiring order so I guessed but I must have wired it wrongly the heating and water runs ok when the thermostat is at 10 but when I increase to over 15 and the thermo clicks everything goes off! my system is an old gloworm ultimate with two mid system mechanical valves the current wires to the thermostat are brown, blue, and earth.

Cheers All
 
Sponsored Links
Dont be so sure that you have an earth , most room stats did not need earthing so the earth wire was used as a switch wire, a simple test with a multi-meter will confirm if it is indeed an earth
 
  • Thanks
Reactions: Ref
How?

Earth wires must NEVER be used for anything other than earth. If it is used as a switch wire, you need to get an electrician to rectify this for you.

Chances are though, you've just gonnected the switched live to the normally closed termial instead of the normally open terminal.

Can you post a photo of the wiring at your room stat?
 
  • Thanks
Reactions: Ref