HELP...glow worm micron 100ff cutting out

Joined
13 Feb 2007
Messages
2
Reaction score
0
Location
London
Country
United Kingdom
Hello everyone,

great forum, thought i'd see if anybody could help me out with a strange problem my boiler is having [i think it might be an early mid life crises or something!]

Problem: Fires up ok, then cuts out after about 5 to 15 seconds, igniter clicks away and burner re-fires, 5 to 15 seconds later cuts out again.....this loop continues for what seems like ages before it finally settles down and heats the house up nicely :-) Once temperature is reached and the boiler stops for a while, the whole process/problem starts again when it's time for it to do it's job.

I serviced it a few weeks ago and all is ok [although I'm not a plumber I am a competent diy'er and an electronics/mechanical engineer] what I did notice thought is that with the front cover removed it works great, put the cover back on and it has a hissy fit straight away, even if I leave a slight gap [i.e. not tighten the screws down] it work great, it seems to be starving of oxygen or something.

I had a plumber look at it over the weekend and he's suggesting replacing the pcb, I can't see this being the problem but I'm not a plumber, so would appreciate suggestions from others who may have suffered with the same problem or know what the fault could be.

Thanking you all for you help in advance.
 
I had a plumber look at it over the weekend and he's suggesting replacing the pcb






Fair enough Micron's have had some board problems. But if I had a pound for every time someone immediately jumps to the conclusion of a faulty PCB, I'd start making PCBs to sell to them.
 
sounds similar to my problem (see my post on cutting in/out) only mine takes about an hour before the problem starts and then doesn't stop till i turn the damn thing off
 
pete not the plumber said:
what I did notice thought is that with the front cover removed it works great, put the cover back on and it has a hissy fit straight away, even if I leave a slight gap [i.e. not tighten the screws down] it work great, it seems to be starving of oxygen or something.
quote]

That would definately point to a fan/venturi/APS problem but NOT the PCB !

As those are safety devices I cannot give you detailed instructions on what needs to be done as that needs a competent person who would normally be CORGI registered.

I would suggest you need a boiler engineer rather than a "plumber" !

Tony
 
Thank for taking the time to reply guys.

Tony, excuse my ignorence, what is an APS? and a venturi? [I know what a 'venturi' is, what i mean is where and what is it on a boiler]

Out of interest the fan was replaced by myself about four weeks ago as the old one became noisy [bearing trouble] but the cutting out problem was alredy there.
 