Help with actuator wiring please!

i did pull the lever on the head for some stupid reason and the trip switch went off and the fuse went on the timer clock
 
Sponsored Links
As that caused a dead short you may have damaged any or all of the contacts in the circuit!

That proves the grey and the blue are reversed though. Swap them over and see what is still working. Check things switch off as well as on, as contacts may now be welded together.

The fuse should be 3Amp! (5 Amp for some oil boilers)
 
Last edited:
thanks it is a 3 amp this might be the wiring diagram for it
image_zpspweonn7k.jpg
 
Sponsored Links
Yes, that also matches with your wiring diagram and makes sense with your first diagram too.
 
I know that's what I was afraid of thanks again and to everyone who replyed
 