I have a single 180x50mm purlin either side of my concrete tiled roof (battens & rafters).
The purlin is about half way down the roof and the plan view of the roof is around 3.4m from the ridge line to the eaves.
Supports for the purlins are around every 2m except some previous owner though it a good idea to remove a couple whilst re-doing the water tank and other works. The result is that one side of the roof has a slight sag due to the 5m unsupported span in this area.
I've commissioned a set of calculations which I am trying to follow and possibly rework with some different values. The reason being that the proposal is to put a single support block to reduce the large span to 3.3m and reinforce that part of the purlin with another 175x75 purlin bolted on. Now there is a possibility of using a different wall for the support block which involves moving/removing the water tank which I probably want to do anyway. So if I can understand the calcs involved I can punch in the different length.
The calcs are (and which all have very little meaning to me) - based on span 3.3m
w = 1.7 x 1.85 = 3.1 KN/m
M(max?) = 3.1 x (3.3 x 3.3)/9 = 3.8 KN/m
Z(xx) = 50 x (180x180)/6 = 270 x 10 to power 3
I(xx) = 50 x (180 to power 3)/12 = 24.3 x 10 to power 6
Therefore sigma = 3.8 x 10 to power 6/270 x 10 to power 3 = 14
and sigma (all) = 5.3 x 1.25 = 6.6 N/m squared
Then after trying the calcs with a 175 x 50 C16 purlin which shows insufficient (sigma = 7.2N/m square) which is too high they are redone with 175 x 75mm C16 giving a sigma of 5.8 which is deemed ok. All handwritten so not easy to read writing either.
Anyhow a bit of help with understanding the process above will enable me to play with the figures a bit. I did Mech Eng and awful long time ago so I assume there are some standard static and dynamic loads as well as standard beam bending moment figures in there somewhere.