help with testing?
3 Oct 2007
Norfolk
Im about to extend a ring main with one double gang RCD socket, im a bit in the fog regarding testing, i understand that i will have to fill out a minor works form? what tests will i need to implement? i have been told that i do not need to do a earth loop or a PSC at the main board for minor works job is this right? my belief by what i have read is i do the following:
Continuety (R1 R2)
Installation resistance (obviously with RCD taken out)
Polarity
Earth Loop at all sockets on cct recording the highest reading
Rcd Test
Continuety (R1 R2)
Polarity
Rcd Test
Ring continuity ( r1 r2 rn & R1 + R2 & will proove polarity if done right)
IR
EFLI
RCD test
just looking at the job i am to do again, i have noticed that the socket i will be extending from has an earth terminal in the back box and not a separate earth wire back to the CU and so obviously uses the metal conduit to earth back to the CU so how would i do a continuity test / installation test back at the board for this, i have read testing books and i cant find what to do?
you can't really do a round the ring continuity test when the conduit is used as earth.
you can however use a lead to test that the earth of each socket is somehow connected back to the CU earth.