Not if he terminates a socket on the end of the cable leaving the connection point.Will that not leave the 2kW oven with an incorrect fuse rating?
diversity is not applied to the circuit protective device, it's applied to the whole installation for design current..
Forthly you should use 4 sq mm cable from there to the 2kW unit (in free air) so that the cable is protected by the 30A fuse. This requires the appliance to be prepared to accept that size cable.
If the 2kW unit has a plug already fitted then the 4mm cable runs to a 13A socket.
diversity is not applied to the circuit protective device, it's applied to the whole installation for design current..
the odds of every heating element being on at the same time for a cooker and hob will be fairly small, however it does happen from time to time, at which point an undersized fuse or breaker will blow / trip..
Oh, take your point - 434.2.1 - less than 3m.