Hi all, I have the following situation at home reference a kitchen refit.
John Lewis:
Hob 7.4kw, Combination micro wave oven 3.45kw and oven 3.68kw. Odd fuse sizes of 15 and 16amp (EU I guess) for the last two but with diversity they'll run at 11.5 and 11.8 amp?
I'm considering feeding all three from original cooker circuit - 6mm T&E off 32amp mcb on rcd bank of board into a 45amp cooker point then into a dual outlet. One side would feed the hob in 6mm then other side would go to a double socket to take the plugs for the m/wave and oven.
Allowing diversity I've come up with a load of 26 amp? correct me please if nec.
The loading appears ok but wondering if I've missed summink, and whether or not it wld be best to maybe put one of the ovens on the kitchen ring?
Ideally Id like to have run a new radial on a new mcb but due to tiled floors etc. almost impossible.
Help would be gratefully received.
Cheers all in advance
Harry
John Lewis:
Hob 7.4kw, Combination micro wave oven 3.45kw and oven 3.68kw. Odd fuse sizes of 15 and 16amp (EU I guess) for the last two but with diversity they'll run at 11.5 and 11.8 amp?
I'm considering feeding all three from original cooker circuit - 6mm T&E off 32amp mcb on rcd bank of board into a 45amp cooker point then into a dual outlet. One side would feed the hob in 6mm then other side would go to a double socket to take the plugs for the m/wave and oven.
Allowing diversity I've come up with a load of 26 amp? correct me please if nec.
The loading appears ok but wondering if I've missed summink, and whether or not it wld be best to maybe put one of the ovens on the kitchen ring?
Ideally Id like to have run a new radial on a new mcb but due to tiled floors etc. almost impossible.
Help would be gratefully received.
Cheers all in advance
Harry