Honeywell motorised valve.

Joined
17 Jan 2016
Messages
93
Reaction score
4
Country
United Kingdom
Is it possible to keep a Honeywell valve in the manual position to provide central heating? My Bosch boiler isn't firing for CH but does for HW and I suspect the valve, although it's only three months old! I am hoping to get an engineer out after the bank holiday but I still need heating.

Thanks.
 
Sponsored Links
Joined
20 Jul 2005
Messages
7,054
Reaction score
1,756
Location
Nottinghamshire
Country
United Kingdom
There's a microswitch inside the valve that starts the boiler when the valve is fully wound across by the motor, the manual lever only part opens the valve and doesn't normally move it far enough to operate the switch. So whilst the valve will be open with the lever in manual, you will find that it probably won't start the boiler.
 
Joined
17 Jan 2016
Messages
93
Reaction score
4
Country
United Kingdom
There's a microswitch inside the valve that starts the boiler when the valve is fully wound across by the motor, the manual lever only part opens the valve and doesn't normally move it far enough to operate the switch. So whilst the valve will be open with the lever in manual, you will find that it probably won't start the boiler.

Thanks. What I have found is that moving the lever to manual starts something off, I can hear it, but the lever quickly returns to automatic.
 
Joined
15 Aug 2010
Messages
25,769
Reaction score
12,177
Location
Livingston
Country
United Kingdom
if you manually latch the valve in the manual position, you will get heating as long as there is a demand for HW, you may need to put the HW to constant and lift off the cylinder thermostat though as once the cylinder is satisfied the CH will also go off
 
Sponsored Links
Joined
17 Jan 2016
Messages
93
Reaction score
4
Country
United Kingdom
if you manually latch the valve in the manual position, you will get heating as long as there is a demand for HW, you may need to put the HW to constant and lift off the cylinder thermostat though as once the cylinder is satisfied the CH will also go off

Thanks. I'll wait for the boiler to be looked at.
 
Joined
17 Jan 2016
Messages
93
Reaction score
4
Country
United Kingdom
Out of interest, when the programmer switches on the CH, do the boiler, pump and valve activate simultaneously or does the boiler fire up first. The Honeywell valve always lights up even when nothing else does.
 
Joined
30 Dec 2018
Messages
12,298
Reaction score
1,733
Country
United Kingdom
Out of interest, when the programmer switches on the CH, do the boiler, pump and valve activate simultaneously or does the boiler fire up first. The Honeywell valve always lights up even when nothing else does.

The sequence is time clock, thermostat, then valve actuator which then finally triggers the boiler and pump. So unless everything else says go, the boiler will not run - you would not want your boiler running, against a closed valve.
 
Joined
17 Jan 2016
Messages
93
Reaction score
4
Country
United Kingdom

Attachments

  • 20210428_195343.jpg
    20210428_195343.jpg
    162.6 KB · Views: 78

CBW

Joined
26 Sep 2019
Messages
12,825
Reaction score
3,849
Location
North
Country
United Kingdom
That is not a Honeywell motorised valve
No mate, the name Myson gives it away :LOL:.

Des, to latch that open, you have to manoeuvre it to the lower position. Is it definitely the valve at fault?
 