the ring is so great, I wonder what other sparks would say if they came across a 16amp lighting circuit wired as a ring in 1mm?
another fantastic idea?
the ring is so great, I wonder what other sparks would say if they came across a 16amp lighting circuit wired as a ring in 1mm?
Code 1, I reckon....If the principle of the ring is so great, I wonder what other sparks would say if they came across a 16amp lighting circuit wired as a ring in 1mm?
They recently had a public debate about ring finals
Code 1 seems a bit OTT, I would think either code 2 or code 4 depending on whether there were any SES or SBC lampholders present.Code 1, I reckon....If the principle of the ring is so great, I wonder what other sparks would say if they came across a 16amp lighting circuit wired as a ring in 1mm?
I think that what you meant to say was that even though you have had accurate, truthful and helpful advice on this site, because it doesn't fit with the decisions you've already made for selfish financial reasons which do not take into consideration the interests of your client, you have decided to ignore it and abuse the people who gave it.seems the moderator needs to get out more as well!! suspended,,,,not that the site is much help is it!!!
OK - that idea of yours (of doing it yourself) is rubbish.all someone had to say was" that idea of yours is rubbish,"
OK - do it like this: http://www.competentperson.co.uk/"do it like this"
I read the one where you said that you were going to take a customer's money for doing the design of an electrical installation despite not being qualified or competent to do so, and despite not being able to certify your design, because you didn't want to pay extra for plasterers.and as for financial reasons did you not read any of the posts??
It may be, but there are legal implications, and if you are acting in a professional capacity you have a duty of care to your clients.jobsworthy,strange world when you cant even stick some cables around a house,,
Try this for a while:GUYS---YOUR ONLY LECYS,,NOT THE RIGHT HAND OF GOD!!!!
am affraid to say but you should stop bigging yourself up,,your not THAT important!!!!! and chill out!!!
hi all,need some advice as my electrician has let me down ,BIG time!!
complete re-furbishment of 3 bed house,inc re-wire.
customer living there(very brave!! ) so need electrics on in various rooms as we go from room to room,and make easy and safe for plastering etc this is the idea i have and welcome your comments!
the consumer unit would look like this;;
bed 1,radial 20 amp mcb with 2.5
bed 2,same
bed 3,same
lounge,same
dining room,same
landing,loft,hall,boiler,house alarm,same
undertile heating(2kw) fire(2kw) and 4 spare sockets,2.5mm ring 32amp
garage,4mm armoured 20amp with second unit in garage with 6 and 16amp
kitchen,32 ring for sockets,and 20 amp radial for washer,dishwasher
6mm for cooker(no socket)
up lights,1.5mm 6amp
down lights,same
bathroom (x2)lights etc ,1.5 6amp (on rcd)
smoke alarm,1.5mm with 3core links 6amp
100amp main switch and 80amp rcd
service fuse 60amp!! looking to have service head replaced to 100amp
should the outside lights be on rcd?have own circuit? there will be about 4
think thats it! any thoughts would be great,,(now off to bury my claw hammer where that lecy cant wire any lights )