How does 1.5mm T&E comply with table 54.7 in BS7671?

Discussion in 'Electrics UK' started by eveares, 20 Apr 2019.

  1. eveares

    eveares

    Joined:
    28 Jul 2012
    Messages:
    1,315
    Thanks Received:
    46
    Location:
    Surrey
    Country:
    United Kingdom
    Table 54.7 in BS7671 says that when the protective conductor is the same material as the line conductor (S), it must at least be the same size as the line conductor.

    Why does 1.5mm² T&E not comply with this reg when you have 1.5mm² line conductors and 1mm² protective/CPC conductor!?

    Can some one explain, my guess table 54.7 does some how not apply to T&E cables.

    Regards: Elliott.
     
  2. Sponsored Links
  3. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,778
    Thanks Received:
    4,246
    Location:
    Retired to:
    Country:
    Portugal
    Table 54.7 is the fail safe option.

    Read 543.1.4.
     
    • Thanks Thanks x 1
  4. eveares

    eveares

    Joined:
    28 Jul 2012
    Messages:
    1,315
    Thanks Received:
    46
    Location:
    Surrey
    Country:
    United Kingdom
    When you fail to read. :oops::notworthy:
     
    • Like Like x 1