How many times do you come across this?
Spot the obvious (missing) thing...
Spot the obvious (missing) thing...
Is there any over current protection on the shower ?
.

Where is the supply to that shower RCD coming from? Clearly not the 'primary' post-meter Henley's - so do I take it that there is another pair of 'secondary' ones just off the right of the piccie? If so, why? - were there not enough 'holes' in the primary ones?That's the one I was hoping would be spotted! It is indeed just a standard Hagar 30mA 40A RCD. No Overcurrent protection at all.
And you think a 5WW could do what has obviously taken a few years for someone to cook up?It might be a DP RCBO, but I think you are right Bernard!
Curses, too slow..
I do see this too often - that's 5DWs for you...
Even if those conditions could be satisfied, I wonder whether the DNO concerned would be happy with a final circuit being protected only by their fuse, even if BS7671 were happy (which I doubt)? westie?If the shower can't overload the cable and the cable can withstand the fault clearance time of the main fuse then no regulations have been breached.