I want to add sockets but....
Once the RCD is fitted alongside the retrofitted MCB's will the consumer unit then be to current regs?
The RCD is fitted to the socket circuits only, NOT the entire board (314.1 refers to installations not having a single point of failure, which would be the result of a single RCD installed in the supply tails for the fuseboard).
Appropriately sized cable from the existing 30A fuse to the RCD, then both ends of the ring connect to the RCD.
How far apart from the original socket are you intending to put the new ones?
If, say, they were to be about an inch or so, you may be able to get a 4 galv conduit couplers and some bushes, fix the old and new back boxes rigidly together, cable through these and no need for the RCD.
It won't matter how close together the sockets are, or what cable is used, or how the cable is installed.
All socket outlets require RCD protection.
ah, the old sweeping generalisation again..
411.3.3 Additional protection
In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
(i) socket-outlets with a rated current not exceeding 20A that are for use by ordinary persons and are intended for general use, and
(ii) mobile equipment with a current rating not exceeding 32A for use outdoors.
An exception to (i) is permitted for:
(a) socket-outlets for use under the supervision of skilled or instructed persons, e.g. in some commercial or industrial locations, or
(b) a specific labeled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.
Oops, yea :oops: i was thinking 'rcd for buried cable' and a cheaper way of dealing with it.
kinda overlooked the 'its for sockets' bit.
To the OP,
Do you need 4 socket outlets in every corner? Would 3 be enough?
http://www.screwfix.com/prods/12362...s/Clipsal-Converta-Skt-2G-to-3G-Polycarbonate
just a thought
That's a good idea, but why not use the 2 to 4 gang version?
http://www.screwfix.com/prods/60887...s/Socket-Converters/1G-to-4G-Sw-Skt-Converter
This will give him the 4 sockets he wanted. I've installed a couple of these, but find they look a bit chunky, but mine are hidden by furniture.
It would mean no chasing, new cable etc. Sometimes a bit fiddly to screw down, but solved by using longer screws.