No central heating/hot water

*Boiler sounds fine

*Re-set button won't press (never has done)

*Pressure was half a bar, released valve and its gone back up to 1 and a half

*Burner light is ON

*Status flashing H 3

*No flow in one of the radiators (you can hear water in all others)

Going to try bleeding the radiators

Tried switching boiler off and on

Thanks in advance for any suggestion's !
 
Sponsored Links
Joined
26 Jan 2012
Messages
53
Reaction score
8
Country
United Kingdom
Definitely PCB issue. May as well replace the thermistor as per course as it will be out of calibration if boiler not serviced for 2 hrs minimum and cheap as chips. No brainer really.
Every other Isar/ Icos I come across is PCB related. Maybe an expensive part but definitely cheaper than a new boiler.
In an Ideal world ay?

There's voices coming through my speakers
 
Joined
22 Feb 2012
Messages
650
Reaction score
118
Location
Sheffield
Country
United Kingdom
May as well replace the thermistor as per course as it will be out of calibration if boiler not serviced for 2 hrs minimum and cheap as chips. No brainer really.

that makes sense
 

CBF

Joined
15 Oct 2012
Messages
2,165
Reaction score
363
Location
Hampshire
Country
United Kingdom
Definitely PCB issue. May as well replace the thermistor as per course as it will be out of calibration if boiler not serviced for 2 hrs minimum and cheap as chips. No brainer really.
Every other Isar/ Icos I come across is PCB related. Maybe an expensive part but definitely cheaper than a new boiler.
In an Ideal world ay?

There's voices coming through my speakers

this makes no sense at all, so are you saying that if you spend two hrs servicing the boiler then the thermistor will be ok ? what has spending two hrs servicing got to do with anything ?
 
Joined
19 Jan 2007
Messages
1,283
Reaction score
171
Location
Kent
Country
United Kingdom
H3 is dhw sensor open curcuit or shorted,make double sure its piped up right way round as some (especially if its a warmfront install) werent.Remove the sensor,and youll get flooded.
Although all should have been rectified by now.
 
Joined
4 Apr 2010
Messages
222
Reaction score
23
Location
Yorkshire
Country
United Kingdom
Just change the DHW thermistor, nothing todo with the pcb. I have changed quite a few thermistors and never changed a PCB due to H3 fault.
 
Sponsored Links

CBF

Joined
15 Oct 2012
Messages
2,165
Reaction score
363
Location
Hampshire
Country
United Kingdom
Just change the DHW thermistor, nothing todo with the pcb. I have changed quite a few thermistors and never changed a PCB due to H3 fault.

yes it's the cheapest thing to try, i've had some with the correct resistance but they are still faulty, however if this doesn't sort the prob then it's pcb so you saying it's nothing to do with pcb isn't correct
 
Joined
28 Oct 2005
Messages
31,282
Reaction score
1,996
Country
United Kingdom
The PCB is a gas related part so the rules forbid you giving out this information.
 
Joined
28 Oct 2005
Messages
31,282
Reaction score
1,996
Country
United Kingdom
Well why do you give info about some parts and not others? :rolleyes:
 