my boiler is on 0(zero) but my radiators are hot?!!? It has been like this all day. I tried resetting it and switching it off but it still has the same problem.HELP PLEASE
 
0 on display is standby no call for heat

methinks you might have a point d :wink:

isn't the dhw thermistor the flow switch as well could be worth a look :idea:
 
ISARs dont have a flow switch unless the pre heat disablement kit has been fitted. The thermistor is ridiculously sensitive to temp change in the plate, hence the problem with 'C' and 'D' cycling with a drip on a tap etc.

Chances are the OPs rads are heating with the hot tap on DV passing.

OP, run a hot tap and feel the far left pipe on the boiler..... if it gets hot thats your problem...
 