Eh? But it is fused down? And even if it weren't, and 1.5 were used, the CCC doesn't change so surely it wouldn't need de-rating.ColJack said:majority of times it would be on it's own 16A or 20A breaker fed with 2.5 and isolated with a double pole switch.. no fusing down, so it should carry on in 2.5..
Softus said:I apologise - I misread your post, and was thinking that there was an FCU involved, i.e. limiting current to 13A. Sorry.
PS Sorry.
I think so.RF Lighting said:Is this any different to a twin socket spurred from a ring circuit though?
The double socket isn't rated at 26A, so it isn't ok; although I take your point that it's ok for the cable, but these loads are attached to fused plugs, so even a fault current in an appliance couldn't exceed the cable CCC.In that scenario you have a cable rated at 27A supplied by a 32A MCB, so the cable is too small for the OCPD, but as the cable only feeds a twin socket, the maximum load that can be drawn on the single 2.5mm² is 26A, which is ok.
But this load is unfused (if wired to a DP switch only) so a fault current could exceed the flex CCC.With the imm heater scenario, there may be a 20A supply to the 20A DP switch fed in 2.5mm², but as the imm heater is a fixed load of 3kW (around 13A), then the most current that can flow on the 1.5mm² flex is 13A, which is ok for the CCC of the flex.