Connected where?I would use a circular 16A plug and socket.
Some certainly don't cope. However, as I imagine is the experience of others, I've seen 3kW immersions that have been fed via a 13A BS363 plug/socket for years, without any signs of a problem.I'll most likely get flak for this but what the hell... I wouldn't feed a 3kW immersion off a 13 amp plug and socket for any length of time as I don't believe they can cope with the continuous full load.
Yes, in reality, probably OK as a temporary measure. Indeed, using your logic, why bother with a plug/socket at all when 3 Wagos would do the job?However, with 1.5mm2 flex feeding the immersion I'd feel quite happy, even on a ring final circuit, to temporarily swap a 13 amp plug and socket to a BS546 15amp plug and socket. Non-standard, yes, but it's a fixed load and any fault will clear on a 30/32A protective device if the circuit is within spec.
I'm not sure that I would put too much money on thatAnd these days, when appliances exclusively have 13 amp plugs, it's not as if there's a risk of an apppliance with a puny flex being unknowingly plugged in and not adequately protected.
There's quite a it to be said for them, the main problem obviously being the lack of a fuse,particularly on 32A circuits.I'm quite a fan of the BS546 plug and think there's still a place for it in domestic / light commercial. I think its potential is under-exploited.
Indeed. People tend to forget that when we're having these discussions about the potential problem of having an immersion fed via a plug socket, when many people seem to think of it as a 'continuous' 3kW (about 13A) load.May seem odd, but often better if not switched off, reason is time the immersion is switched on for ..... once the water is hot, the time the immersion works to re-heat water is shorter, so plug heat wise leaving on is likely better.
... which, of course, is a very common location.If plugged in where there is free air not so much of a problem, the problem is were inside an airing cupboard.
That is undoubtedly very often the case.I think the problem is just that the individual socket and plug might be faulty (loose) rather than any complicated physics, locations, calculations or anything else.
Research by ourselves and third party organisations has shown that all MK double sockets can safely withstand a continuous load of 19.5A for an indefinite period. Increasing the load slightly will begin to cause heat and mechanical stresses on the components in a relatively short period. Testing showed that a load of 22.3A was sufficient to cause heat stress that would cause a browning of the faceplates and sufficient heat to cause insulation damage to cable cores. A load of 24A for 43 hours was sufficient to cause significant heat damage to the material in which the socket-outlet was situated and within 75 hours sufficient to cause significant damage that would lead to the very real potential of fire.
I realised that, but I was just making the point that the capabilities of plugs/sockets may not necessarily be what one would (I would say 'reasonably') expect. As you go on to say ...I was thinking more of a single socket for the immersion - but - apart from that -
Quite so - and I would say that applies to a socket with two "13A outlets", which one certainly would not expect to suffer "... significant damage that would lead to the very real potential of fire." whilst carrying 24A total (even if for 75 hours), doesn't it ?surely manufacturing a product, into which a quite reasonable unsuspecting person can attach two 13A devices and loads, which cannot cope with that load (not to mention the extra current until a protective device would operate) is a negation of duty and a deception on the public.
Exactly -as above.So, in view of the quote, then it is not surprising that some sockets and plugs fail because they were not made well enough.
Yes, indeed.Quite so - and I would say that applies to a socket with two "13A outlets", which one certainly would not expect to suffer "... significant damage that would lead to the very real potential of fire." whilst carrying 24A total (even if for 75 hours), doesn't it ?
As you say, "yes, indeed".Yes, indeed. It is rather strange that the manufacturers are allowed to get away with it.
... which would 'almost' be OK. However, as many of believe, it is (or should be) 26A then, as you say, in view of what they have written, I don't understand why they are "allowed to get away with it" - apart from anything else, it would sound like a Trading Standards issue to me.all MK double sockets can safely withstand a continuous load of 19.5A for an indefinite period
None 'as bad as' this one come immediately to my mind.Is there anything similar - something apparently obvious but not?
I can but agree.We think (know) cable rated at 27A will not only be able to carry 27A 'for ever' but also cope with the over-current caused by the fusing factor of protective devices. Yet sockets will cause a fire.
Even that might not be a total solution, if the metal socket got hot enough 'to start a fire'!Better have only metal sockets.
Even if the cylinder starts off totally cold (very rare), it only takes about 2.4 hours.
That obviously depends upon the degree of ventilation and other means of heat loss. In the absence of means of 'getting rid of the heat' as fast as it was being produced, the temperature would continue to rise 'indefinitely' - so by no means guaranteed to reach a peak in 15 mins.I would judge it might only take an over-heating 13amp plug and socket, 15 minutes to hit their peak temperature...
That's reasonable enough, but would you say the same if the immersion was connected via, say, a DP switch - which, if the connections were loose enough, could get very hot very quickly? ... and what about cooking appliances?, so I personally would be quite wary of leaving such an arrangement unattended until it had proved itself.