    Just a quick question.

    I've got a side entry immersion on an unvented tank There's actually two elements but just one in use as there's no E7. The immersion thermostat is of a type with spade terminals that push onto the heater element. I'm aware that a replacement must have an over temp trip, but are these thermostats all the same or manufacturer specific? I'm thinking that the dimensions may vary and not necessarily marry up to the orifice and heater terminals.

    Thanks.
     
  2. Sponsored Links
  3. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,630
    Thanks Received:
    2,141
    Location:
    Oxfordshire
    Country:
    United Kingdom
    It depends on the make. Which unvented tank is it?
    Some tanks have an over temp cut out separate to the immersion itself.
     
  4. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,932
    Thanks Received:
    1,780
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    I would not think they would be the same, as those which are used with alternative heating have reset button, but those which are the only control have non re-settable over temp, so if thermostat fails it must be changed, you would not want that if the solid fuel heating could trip the electric over temperature cut-out.
     
  5. Johnmdc

    Johnmdc

    Joined:
    5 Jun 2015
    Messages:
    350
    Thanks Received:
    102
    Location:
    Bolton
    Country:
    United Kingdom
    I take it that the thermostat is faulty if so then why not just use the thermostat out of the unused one?
     
    Last edited: 12 Jul 2020
    • Like Like x 1
  6. JulianP

    JulianP

    Joined:
    1 Dec 2013
    Messages:
    121
    Thanks Received:
    16
    Location:
    Cumbria
    Country:
    United Kingdom
    That is a good point, but they're about 10 years old and I have an idea that an electrician already did that some years ago so I would like a spare. It's for a tenanted property. The safety trip had tripped on it, I reset it easily enough but I'm no convinced if it won't trip again. Although someone had wound the normal adjustment to full hot so that won't help.
     
  7. JulianP

    JulianP

    Joined:
    1 Dec 2013
    Messages:
    121
    Thanks Received:
    16
    Location:
    Cumbria
    Country:
    United Kingdom
    The OT is on the 'stat. Why would the tank manufacturer be of significance? Isn't the thread form for side entry immersion heaters the same for them all?
     
  8. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,630
    Thanks Received:
    2,141
    Location:
    Oxfordshire
    Country:
    United Kingdom
    I ask because I had to replace a stat for a Megaflo unvented tank. It was a specific type and nothing like your regular immersion stat.

    Maybe it would be easier if I ask you the question in a different way:
    Is this a Megaflo tank?
     
    • Like Like x 1
  9. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    10,110
    Thanks Received:
    2,039
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    The thread might be, but there are different manufacturers of immersion heaters and thermostats. Some might be compatible, others not.
    All unvented cylinder immersion heaters have an over temperature cutout in them. That may be part of the thermostat, of it may be a separate device adjacent to the thermostat.

    If you need a new thermostat, get an identical one from the same manufacturer.
     
  10. Sponsored Links
  11. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    26,044
    Thanks Received:
    2,595
    Location:
    Bedfordshire
    Country:
    United Kingdom
    As I recall it the immersion heater is required to have a safety over temperature cut out as part of the the thermostat in the immersion heater.
    This cut out has to be manually reset if it trips.

    It makes sense to have that cut out in the immersion thermostat rather than rely on the cylinder thermostat to shut the electric heater OFF.

    If the cylinder was empty then a faulty immersion thermostat could allow the immersion heater get red hot if there was no safety cut out.
     
  12. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,630
    Thanks Received:
    2,141
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Example. Megaflo stat.
    The spade connectors on the back push on to female contacts on the immersion housing.

    EE6FFC80-B609-42DD-B00B-C66A6951441C.jpeg
     
  13. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,186
    Thanks Received:
    3,247
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    It appears that one can still get ones without an integral cut-out ...
    upload_2020-7-12_14-16-40.png

    It's always rather surprised me that the cut-outs are usually part of the thermostat, rather than separate and 'independent' (i.e. part of the element etc.). In the absence of any other source of heating, the cutout is presumably only relevant if the thermostat itself fails, and it if failed in some sort of catastrophic fashion, I would have thought that there would be a risk that an integral cut-out would also become non-functional.

    Kind Regards, John
     
  14. JulianP

    JulianP

    Joined:
    1 Dec 2013
    Messages:
    121
    Thanks Received:
    16
    Location:
    Cumbria
    Country:
    United Kingdom
    Yes, that's the correct idea, it just pushes on to the heater contacts, a neat idea. But I do not know if I have a ''Megaflo'' 'stat as it's 70 miles away at the moment! This particular type of thermostat seems standard for side entry heaters, I'm still not sure if they are dimensionaly standard or not. The usual places all list these things and without trying it for size it's hard to say.
     
  15. JulianP

    JulianP

    Joined:
    1 Dec 2013
    Messages:
    121
    Thanks Received:
    16
    Location:
    Cumbria
    Country:
    United Kingdom
    What I can tell you is this, having tested the thermostat with my multimeter: The regular contacts that cycle the power to maintain temperature break the connection between live supply and heater input. The overtemp trip contact breaks the supply from heater return to neutral. So in a way it is two separate units, just within the same unit.
     
  16. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,186
    Thanks Received:
    3,247
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Sure, one would obviously expect there to be two separate mechanisms but, as I said, and given that both are within close proximity in the same small space, I would have thought that it was not impossible that a 'catastrophic failure' (e.g. thermal damage) could probably disable both.

    Kind Regards, John
     
  17. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page