    Has any one out there got any ideas why my boiler is heating up my hot water the pump remains on the boiler fires up every short while, then of mean while the pump is merrily running away and by the end of the day the water is really very HOT. I have just fitted a Hive Active 2, double checked and triple checked the wiring positions as per listed on the Wiring Centre. The central heating is working fine. Any Help will be Gratefully Received.

    Martin
     
  2. Sponsored Links
  3. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    20,628
    Thanks Received:
    8,023
    Location:
    Lanarkshire
    Country:
    United Kingdom
    we will need a lot more information, boiler make and model, S or Y plan? do you have a cyl stat ?
     
    • Thanks Thanks x 1
  4. RigidRaider

    RigidRaider

    Joined:
    9 Aug 2006
    Messages:
    1,727
    Thanks Received:
    68
    Location:
    Lancashire
    Country:
    United Kingdom
    Have you actually measured the temperature of the water at the tap?
     
    • Thanks Thanks x 1
  5. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    17,467
    Thanks Received:
    1,617
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    I have not looked at Hive software, but often there is anti legionnaires software built in which will every so often heat the water to over 65°C. I had it with Nest, could not work out why when nothing set to run, central heating boiler was on, found it could be disabled and that's what I did, it seems this is quite common.
     
    • Thanks Thanks x 1
  6. Martin Cannon

    Martin Cannon

    Joined:
    22 Oct 2019
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    Good evening all.

    So it is a;

    Y Plan.
    Yes the is a cylinder thermostat.
    Brand new 3 way valve.
    Fully pumped.

    Full story, summer time, hot water working fine, 4 weeks ago tried the heating, would only come on when the HW was off, hence new 3 way valve. Still the same problem, so thought programmer, bought a Hive Active 2, fitted and here i am asking for help............ CH working fantastic, HW working but not as i think it should and or was. If it should work like this with a Hive, please let me know!!!!!!!

    Legionnaires, i will ask Hive.

    Water temp at the tap, really very hot.

    Martin
     
  7. Sponsored Links
  8. Martin Cannon

    Martin Cannon

    Joined:
    22 Oct 2019
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    Sorry Boiler is a Baxi Solo 18 HE.
     
  9. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    17,467
    Thanks Received:
    1,617
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    Y plan default is hot water, if the white wire is powered then it goes mid way, and if white and grey are powered it goes all the way and stops water to DHW. mid-position-valve.jpg So if you lose connection to grey then can't turn DHW off. This shows how it works.
     
  10. Martin Cannon

    Martin Cannon

    Joined:
    22 Oct 2019
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    So tomorrow I will check and make sure that I have not screwed on to the insulation of the wires and not just that they are in the correct position.
     
  11. RigidRaider

    RigidRaider

    Joined:
    9 Aug 2006
    Messages:
    1,727
    Thanks Received:
    68
    Location:
    Lancashire
    Country:
    United Kingdom
    Have you actually measured the temperature of the water at the tap? It should be around 60c.
     
  12. wwwebber

    wwwebber

    Joined:
    5 May 2004
    Messages:
    432
    Thanks Received:
    24
    Country:
    United Kingdom
    Hive doesn't control your hot water temp - it just schedules when your boiler can heat it.
     
  13. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page