When a TT Supply enters a building doers it have to go directly into a plastic RCD incoming box before entering a metal CU? Its just the Guy from NIC the other dau said it would be against regs because not supplementary proected by RCD if 1st RCD was in Metal CU
There are issues with entering a metal clad CU on a TT - if the tails become damaged (most likely at the point of entry to CU), there is no earth fault protection, and the CU could become live (along with everything else). If the EFL was high, as expected on a TT, the supply fuse would sit happily.
The NIC have a guide which shows a special grommet used to protect the tails on entering a metal clad CU, but I would still prefer an RCD in an insulated enclosure first.......what am I saying.......I would prefer a TN-s or TN-c-s earthing syste first!
So if the TT system came from the supply fuses (3Phase) in2 henley blocks, then tails from the blocks into metal CUs, what would be best action to make safe and to NIC guidlines? Would installing a 3 Phase RCD in plastic CU which supplied Blocks be ok? If CU had a 30mA RCD instead of the required min 100mA RCD is that still ok for a Incomer?
I was under the impression that the normal way of doing caravan sites from a PME supply was to use the PME earth for the distribution network arround the site and only switch to TT at the sockets.
It depends how big a site you are talking of, the one I was thinking about was only a tiny one with 6 outlets. The 3 phases were split over the 3 (single phase) posts. The 3 RCDs & 6MCBs were housed in a central location and were connected as a TT system.
Afaik on a larger setup it is acceptable to use a TT system with 100mA or greater type S RCDs for distribution circuits, the outlets must be protected by a 30mA device (iirc 3 outlets max per RCD).